Re: Facility Sizing (2 feedstock types) + 1MW energy distribut
The grounded (neutral) service conductor shall be sized to safely carry the maximum ground-fault current likely to be imposed on it from where a ground-fault may occur [110.10]. This is accomplished by sizing the grounded (neutral) conductor in accordance with Table 250.66, based on the total area of the largest ungrounded (hot) conductor. In addition, the grounded (neutral) conductors shall have the capacity to carry the maximum unbalanced neutral current in accordance with 220.22. Figure 41 250-24B1 01.cdr.